You will have to excuse my question if it seems simple, I am still new to fire sprinkler design.
We are sprinklering a combustible attic space in an Ordinary 1 building. The building footprint is 1690 ft2.
The sprinkler system is a preaction system, and the roof slope is larger than 1/6, so the design area is required to be 2850 ft2.
Since the attic space (after taking account of the roof slope) is less than the design area, should a portion of the floor space below the ceiling be included to meet the 2850 ft2?
The code says that you only have to go the extent of one floor if it is less than the required design area, but does this apply to attic spaces?
Thanks