This may also be the case with something related to design areas. I have a contractor who is required to design to 1,800 ft2 design area.
He chose two design areas on the same floor. An 1,800 ft2 light hazard area. In a separate design area, he chose 1,200 ft2 of Ordinary 1, the limits of a mechanical rooom, withOUT any adjacent light hazard area
The project must meet UFC 3-600-01 which disallows the room design method. He is claiming that 11.1.2 (extension of design area into adjacent ceiling space) somehow means he only has to calculate for 1,200 ft2 design area.
To me this is patently wrong, however since the result of my review comments will result in chaning out the fire pump and possibly changes to the underground, I wanted to be double dang sure since this is a NICET IV. I am not missing anything am I?
He claims that the 1,200 ft2 OH1 mechanical room in addition to 600 ft2 of adjacent light hazard will push this project over the limit.. I haven't run the numbers yet to check.
TIA