ajitjose
Electrical
- Nov 26, 2017
- 9
I am new to sprinkler design.
Can you guide me how to do a hydraulic calculation for an area less than the minimum required area?
For example, for Extra Hazard group 2, min density and area =232m2 @ 16.3 mm/min. Consider my room is 96 m2. What will be the minimum flow for an area of 96 m2 ?
The below is from NFPA. Can anyone explain to me? I could not follow it. As per my understanding, Step 3 will always be greater than 0 and I didn't understand the rest of it.
23.4.4.2.4* Where the available floor area for a specific area/
density design criteria, including any extension of area as required
by 11.1.2 and Section 12.3, is less than the required
minimum design area, the design area shall be permitted to
only include those sprinklers within the available design area.
A.23.4.4.2.4 The following steps outline the procedure for
calculation in accordance with 23.4.4.2.4:
(1) Calculate the hydraulic design discharge including those
sprinklers within the available floor area.
(2) Calculate the minimum required discharge by multiplying
the required design density times the required minimum
design area.
(3) Subtract the discharge calculated in Step 1 from the discharge
calculate in Step 2.
(4) Where the discharge calculated in Step 3 is greater than 0,
the hydraulic design discharge is recalculated including
an additional flow equal to that calculated in Step 3. The
additional flow is added at the point of connection of the
branch line to the cross main furthest from the source.
(5) Where the discharge calculated in Step 3 is less than or
equal to 0, the hydraulic design discharge is as calculated
in Step 1.
Regards,
Ajit Jose
Can you guide me how to do a hydraulic calculation for an area less than the minimum required area?
For example, for Extra Hazard group 2, min density and area =232m2 @ 16.3 mm/min. Consider my room is 96 m2. What will be the minimum flow for an area of 96 m2 ?
The below is from NFPA. Can anyone explain to me? I could not follow it. As per my understanding, Step 3 will always be greater than 0 and I didn't understand the rest of it.
23.4.4.2.4* Where the available floor area for a specific area/
density design criteria, including any extension of area as required
by 11.1.2 and Section 12.3, is less than the required
minimum design area, the design area shall be permitted to
only include those sprinklers within the available design area.
A.23.4.4.2.4 The following steps outline the procedure for
calculation in accordance with 23.4.4.2.4:
(1) Calculate the hydraulic design discharge including those
sprinklers within the available floor area.
(2) Calculate the minimum required discharge by multiplying
the required design density times the required minimum
design area.
(3) Subtract the discharge calculated in Step 1 from the discharge
calculate in Step 2.
(4) Where the discharge calculated in Step 3 is greater than 0,
the hydraulic design discharge is recalculated including
an additional flow equal to that calculated in Step 3. The
additional flow is added at the point of connection of the
branch line to the cross main furthest from the source.
(5) Where the discharge calculated in Step 3 is less than or
equal to 0, the hydraulic design discharge is as calculated
in Step 1.
Regards,
Ajit Jose