I've designed a number of foundations for Modular Houses (different from Manufactured Housing in that a chassis is not built into the structure of the home). Generally, the factory modular plans contain a loading diagram with reaction values and dimensioned locations. Pretty strait forward.
On a recent plan, the factory provided a foundation plan with moment reactions in lieu of tension loads. Some of their walls are segmented and some appear to be perforated. But they refuse to provide the uplift values or their locations. They inisit I use the non-stamped factory build plans, plus the engineering calculations from the factory, in conjunction with their foundation plan to interpret where the reactions are and what are their values.
Question 1) Assuming that the listed shear walls are part of a continuous rim joist, is there a method for providing holdowns along at intermitant points along the length of the rim to the foundation using the moment? My apprehension is twofold: On one side of the pendulem, the outermost holdowns are not sufficient to take the full tension loads from the full length of the shear wall/rim combination, the outermost connections would tend to fail, increasing the demand on the next connection toward the compression side, and so forth. On the other side of the pendulum, I think "contiunous" holdown support of the rim would work...but not sure how to qualify the solution. Any comments or suggestions?
Question 2)Should the factory be required to provide stamped drawings listing the precise locations of their reactions and the value of their reactions? Seems if they are not willing to provide a stamped response, and qualify unstamped drawings and responses as "for information only," that I'm taking some high risk in assuming their interpration of their engineer's work is accurate. Any other comments?
Thanks for your assistance!
On a recent plan, the factory provided a foundation plan with moment reactions in lieu of tension loads. Some of their walls are segmented and some appear to be perforated. But they refuse to provide the uplift values or their locations. They inisit I use the non-stamped factory build plans, plus the engineering calculations from the factory, in conjunction with their foundation plan to interpret where the reactions are and what are their values.
Question 1) Assuming that the listed shear walls are part of a continuous rim joist, is there a method for providing holdowns along at intermitant points along the length of the rim to the foundation using the moment? My apprehension is twofold: On one side of the pendulem, the outermost holdowns are not sufficient to take the full tension loads from the full length of the shear wall/rim combination, the outermost connections would tend to fail, increasing the demand on the next connection toward the compression side, and so forth. On the other side of the pendulum, I think "contiunous" holdown support of the rim would work...but not sure how to qualify the solution. Any comments or suggestions?
Question 2)Should the factory be required to provide stamped drawings listing the precise locations of their reactions and the value of their reactions? Seems if they are not willing to provide a stamped response, and qualify unstamped drawings and responses as "for information only," that I'm taking some high risk in assuming their interpration of their engineer's work is accurate. Any other comments?