Hello all,
I'm planning to develop a suitable 20kV distribution network in an area of Djibouti to feed small industrial units and ware house located in a certain area .Max .load requirement of per industrial units is around 700kVA and small units requirements starts from 50kVA .
Total load power requirement of the total area is about 5.5MVA .
Djibouti EDD have HT distribution voltage level are 20 kV and agree to give two cable for our area network to form a
ring network .
My proposal in my mind is to strategically locate pocket substation consists of ring main units ( 2F +1 T ee off ) with transformer of 20/.4kV , 1500kVA/1000kVA/500kVA in a ring circuit formed by EDD 2 Cables.I presume the 2 cables can be paralleled as it's feeding from same EDD substation .
.Both the EDD incoming cables are connected to a 2F + 2 T RMU and from 2Tee off swiich with breaker protection feed the next located located 2F+1 T RMU indiviudually and so on the connected to a 4 or 5 more RMU's located different places
I would like to have your inputs on the following .
1) What kind of protection I need to consider in each Ring in Ring out Switches or the protection on the Transformer feeder .
2) I'm prefer to give an O/C protection and E/F indication on each RMU on the T -off unit and Ring IN and Ring Out will be Switches with SF6 insulated .
regards ,
Rana .
I'm planning to develop a suitable 20kV distribution network in an area of Djibouti to feed small industrial units and ware house located in a certain area .Max .load requirement of per industrial units is around 700kVA and small units requirements starts from 50kVA .
Total load power requirement of the total area is about 5.5MVA .
Djibouti EDD have HT distribution voltage level are 20 kV and agree to give two cable for our area network to form a
ring network .
My proposal in my mind is to strategically locate pocket substation consists of ring main units ( 2F +1 T ee off ) with transformer of 20/.4kV , 1500kVA/1000kVA/500kVA in a ring circuit formed by EDD 2 Cables.I presume the 2 cables can be paralleled as it's feeding from same EDD substation .
.Both the EDD incoming cables are connected to a 2F + 2 T RMU and from 2Tee off swiich with breaker protection feed the next located located 2F+1 T RMU indiviudually and so on the connected to a 4 or 5 more RMU's located different places
I would like to have your inputs on the following .
1) What kind of protection I need to consider in each Ring in Ring out Switches or the protection on the Transformer feeder .
2) I'm prefer to give an O/C protection and E/F indication on each RMU on the T -off unit and Ring IN and Ring Out will be Switches with SF6 insulated .
regards ,