Design of boiler blowdown piping

Status
Not open for further replies.

yama21250

Mechanical
Oct 3, 2017
6
Does boiler blowdown piping need to have sweep elbows (3 x radius) or double 45* elbows? I have some info from a boiler inspector requesting this on our blowdown piping but can not find any documentation to support this.

Thanks!
 
Replies continue below

Recommended for you

May check the AMSE B31.1 Power Piping Code for the design requirements of the Boiling blowdown piping for your system.
 
B31.1 Section 122.2 has a should statement for 3D pipe bends.

 
"...should..." and "must" are two different animals.
 
From 2016, B31.1 Section 100.2
should: “should” or “it is recommended” is used to indicate that a provision is not mandatory but recommended as good practice.

suggest using good engineering judgement as you likely know the overall system layout and requirements.
 