mitch0816
Structural
- Oct 27, 2012
- 6
Hi All,
I need to calculate whether or not the bolts used to attach a fence to the face of a retaining wall are adequate to accommodate applied loads (primarily dead load of fence, wind load, and vandal load). Due to existing services in the ground meaning that the fence posts could not be embedded in a certain area, the contractor instead bolted the fence to the face of an existing retaining wall structure (~1.5m high).
The fence will be attached to either UC or SHS posts which are then bolted to the retaining wall (see attached photo of corner section for example).
Can you please suggest a method of calculating the adequacy of this design? How would you suggest calculating pull out force on each bolt?
If additional information is required, let me know and I can provide.
Thank you in advance!
I need to calculate whether or not the bolts used to attach a fence to the face of a retaining wall are adequate to accommodate applied loads (primarily dead load of fence, wind load, and vandal load). Due to existing services in the ground meaning that the fence posts could not be embedded in a certain area, the contractor instead bolted the fence to the face of an existing retaining wall structure (~1.5m high).
The fence will be attached to either UC or SHS posts which are then bolted to the retaining wall (see attached photo of corner section for example).
Can you please suggest a method of calculating the adequacy of this design? How would you suggest calculating pull out force on each bolt?
If additional information is required, let me know and I can provide.
Thank you in advance!