Elsewhere you wrote;
"The 2002 (limit state) code specifies that a 2000 year wind event is used for ultimate design"
AS/NZS1170.0 refers us to the BCA for probability of exceedance to be used for design.
BCA table B1.2 directs us to use 1:500 for wind for 'normal' buildings.
Is there a reason why you use 1:2000?