Hello. I am attempting to get a building permit for a a home renovation (my own home). The HVAC system is not being touched but I do intend to install a new outside-venting 600 CFM max fan over a gas rangetop. I rec'd a deficiency letter from the permit office because of concern over house depressurization associated with the fan. My house is old (1960s) so I know there will be a fair amount of leakage.
Depressurization as I understand it has two main concerns associated with it. 1) Backdrafting of chimney exhausted gas appliances and/or solid fuel appliances and 2) comfort of the occupants. (Soil gas can also be a problem but not where I am)
I have no appliances of the type described in 1).
So my plan is to install a make-up heated air system that is locked to the fan operation, but I am limited in both physical space and capacity on my electrical panel.
So knowing just enough to be dangerous, I found an HRAI form that gives an air infiltration flow based on floor area, a flow factor, and an allowable pressure drop. Floor area is 2600 sq.ft (both floors + basement + half of crawl space is permitted) x 2.5 ACH (old house) x 0.037 (flow factor associated with -10 pa). Or 2600x2.5x.037 = 240 CFM.
So if that is a valid approach I have 360 CFM to make up. However the 600 CFM hood fan will not generate 600 CFM with a deltaP of 10 pa. How do I determine what the flow rate might be reduced to?
As well their is downstream ducting from the fan: 1 foot of 6" pipe, one 90 degree elbow and then an exhaust cap - assume some small pressure loss will occur there too?
In order to make up the ~360 CFM I plan to install a FANTECH MUAS750 along with a 6kw heater - the MUAS750 is rated for 750 CFM max and can be set to provide air so that a slight (-5, -10 pa) pressure is maintained. That device has an 8" collar, but I need to run the ducting from the ceiling of the first floor to the basement as 6" round (or maybe rectangular, but assume round for now). That run is intake + two eight foot sections of 6" pipe and two 90 degree elbows and then would be transitioned to an 8" duct before feeding the MUAS. The downstream ducting will be large in size so can be ignored for now. How can I determine if 6" line is ok from a deltaP/code point of view? A 6KW heater should provide a deltaT of 6/360*3193 = 53F/30F for 360 CFM, so I should be ok there. I need to design for a -18C day, that still gets me to +12C.
Any thoughs/help/etc? Am I way off base? I should note that the fan is capable of 600CFM bust has four speeds. The high speed/flow would only be used rarely.
Thanks.
Jeff
Depressurization as I understand it has two main concerns associated with it. 1) Backdrafting of chimney exhausted gas appliances and/or solid fuel appliances and 2) comfort of the occupants. (Soil gas can also be a problem but not where I am)
I have no appliances of the type described in 1).
So my plan is to install a make-up heated air system that is locked to the fan operation, but I am limited in both physical space and capacity on my electrical panel.
So knowing just enough to be dangerous, I found an HRAI form that gives an air infiltration flow based on floor area, a flow factor, and an allowable pressure drop. Floor area is 2600 sq.ft (both floors + basement + half of crawl space is permitted) x 2.5 ACH (old house) x 0.037 (flow factor associated with -10 pa). Or 2600x2.5x.037 = 240 CFM.
So if that is a valid approach I have 360 CFM to make up. However the 600 CFM hood fan will not generate 600 CFM with a deltaP of 10 pa. How do I determine what the flow rate might be reduced to?
As well their is downstream ducting from the fan: 1 foot of 6" pipe, one 90 degree elbow and then an exhaust cap - assume some small pressure loss will occur there too?
In order to make up the ~360 CFM I plan to install a FANTECH MUAS750 along with a 6kw heater - the MUAS750 is rated for 750 CFM max and can be set to provide air so that a slight (-5, -10 pa) pressure is maintained. That device has an 8" collar, but I need to run the ducting from the ceiling of the first floor to the basement as 6" round (or maybe rectangular, but assume round for now). That run is intake + two eight foot sections of 6" pipe and two 90 degree elbows and then would be transitioned to an 8" duct before feeding the MUAS. The downstream ducting will be large in size so can be ignored for now. How can I determine if 6" line is ok from a deltaP/code point of view? A 6KW heater should provide a deltaT of 6/360*3193 = 53F/30F for 360 CFM, so I should be ok there. I need to design for a -18C day, that still gets me to +12C.
Any thoughs/help/etc? Am I way off base? I should note that the fan is capable of 600CFM bust has four speeds. The high speed/flow would only be used rarely.
Thanks.
Jeff