I was asked to detailed easy-to-follow operational procedures which will assure that the NEMA 1-start hot / 2-starts cold requirement will not be violated (for one specific motor). In other words, a set of rules which a non-motor person could use to evaluate any postulated operation scenario start1/run1/stop1/rest1/ start2/run2/stop2/rest2/ start3/run3/stop3/rest3/ etc (with specific durations given for run1, rest1, run2, rest2, run3,rest3 etc) in order to determine whether the scenario meets the NEMA requirement one start hot/2-starts cold.
You'd think that would be easy. Maybe I'm slow today, but it's difficult for me to come up with the specific procedure.
The motor in question takes about 3 hours for stator temperature to cool 66% of the way to its final temperature after being secured. It also takes only one half hour to reach its final temperature after being started (as expected the time constant is much longer while secured than while running). I don't have access to any rotor temperatures of course.
My goal is simplicity and meeting the NEMA guideline. If I end up being a little overly restrictive, that would be ok.
Here's my discussion / conclusion.
I think this meets the intent of the NEMA requirement. What do you think.
Would you have an alternate suggestion for specific procedures to assure the NEMA guideline is met?
Would you have an alternate suggestion for specific procedures for limiting of large motors when OEM has not provided any repetitive starting limitation information other than the NEMA requirement?
=====================================
(2B)+(2B)' ?
You'd think that would be easy. Maybe I'm slow today, but it's difficult for me to come up with the specific procedure.
The motor in question takes about 3 hours for stator temperature to cool 66% of the way to its final temperature after being secured. It also takes only one half hour to reach its final temperature after being started (as expected the time constant is much longer while secured than while running). I don't have access to any rotor temperatures of course.
My goal is simplicity and meeting the NEMA guideline. If I end up being a little overly restrictive, that would be ok.
Here's my discussion / conclusion.
electricpete proposal said:Discussion:
NEMA MG-1 specifies one start hot / two starts cold.
The intent of one start hot / two start cold is that we only ever restart the motor once from any condition other than “ambient”. After we use up that start, we have to wait for it to cool to ambient.
For example if motor is initially cold, we start it and it trips, we can attempt restart. (this is our allowance two starts cold). Any further starts cannot occur until after the motor is cooled to ambient.
If motor is running for a long period of time and then is secured or trips, we can restart it before it cools but only once. (one start hot allowance). Any further starts cannot occur until after the motor is cooled to ambient.
How long it takes for the motor to cool to ambient after it is secured is not well defined. My judgement based on review of the stator winding temperature trends is this interval is 3 hours for the motor under consideration.
Conclusion:
In general, all starts of this motor should be spaced at least 3 hours apart. If we find occasion where we need two starts (start #T and start #T-1) to be less than 3 hours apart, we can do that provided the first of these two starts (#T) was separated at least 3 hours from the start before that (start #T-1).
I think this meets the intent of the NEMA requirement. What do you think.
Would you have an alternate suggestion for specific procedures to assure the NEMA guideline is met?
Would you have an alternate suggestion for specific procedures for limiting of large motors when OEM has not provided any repetitive starting limitation information other than the NEMA requirement?
=====================================