This thread goes along with another thread I currently have ongoing but shifts topics a bit so figured I'd start a new thread to discuss.
The issue here is weather or not the generator backup protection 51V/50P and plant distribution feeders 50/51 elements will be able to detect faults at the utility. This application again has a 2MW generator at 4.16kV connected via a feeder with 50/51 to the main plant bus which then connects to the utility service through a main breaker with 50/51. The plant service is coming in through a 22.8kV-4.16kV transformer which I am being told is 10MVA and currently trying to obtain more information as to the impedance and winding configuration. Others have indicated that that there is not a need for a 67 element at the plant's main breaker to detect faults at the utility because these faults will be detected by the generator backup protection as well as the plants feeder and main 50/51 elements.
My concern however is for faults that may occur on the utility side of the service transformers and weather or not these protection elements will see these faults. I just don't see this backup protection being able to detect and disconnect the generator for faults that may occur on the utility system. The 51V element has a pickup of 600A while the feeder breaker and main breakers have 50/51 pickups of 400A and 2000A respectively (assuming that these 50/51 elements will see current in the reverse direction for faults at the utility and don't just see fault current in the forward direction)
When running a quick simulation with an assumed transformer impedance (using 10MVA rating) I come up with a reverse current flow through the transformer of 400A for faults on the utility side of the transformer supplied from the plant generator (ignoring plant motor contribution). Looking at this, it appears that the feeder breaker and main breaker 50/51 elements would not pickup for this fault flow however I'm not sure if the 51V element would detect this fault? Would the voltage collapse at the utility be enough to pickup the 51V for faults on the utility side of the transformer?
Also I'm still waiting to confirm the utility transformer winding configuration but if its a Delta-Wye configuration then the plant feeder or generator backup protection will not be able to see ground faults that occur on the Utility Delta side of the transformer. In this case would a 67N definitely be needed to detect these faults? If the transformer is a wye-Wye configuration then can the generator 50/51N and 501G as well as the plants feeder 50/51N see these external faults?
Maybe I'm incorrect here in assuming that the generator needs to trip for faults occurring on the utility side of the transformer but if it does not, then I see issues occurring when the utility re-closer tries to reclose and the generator is still online.
I appreciate any thoughts.
The issue here is weather or not the generator backup protection 51V/50P and plant distribution feeders 50/51 elements will be able to detect faults at the utility. This application again has a 2MW generator at 4.16kV connected via a feeder with 50/51 to the main plant bus which then connects to the utility service through a main breaker with 50/51. The plant service is coming in through a 22.8kV-4.16kV transformer which I am being told is 10MVA and currently trying to obtain more information as to the impedance and winding configuration. Others have indicated that that there is not a need for a 67 element at the plant's main breaker to detect faults at the utility because these faults will be detected by the generator backup protection as well as the plants feeder and main 50/51 elements.
My concern however is for faults that may occur on the utility side of the service transformers and weather or not these protection elements will see these faults. I just don't see this backup protection being able to detect and disconnect the generator for faults that may occur on the utility system. The 51V element has a pickup of 600A while the feeder breaker and main breakers have 50/51 pickups of 400A and 2000A respectively (assuming that these 50/51 elements will see current in the reverse direction for faults at the utility and don't just see fault current in the forward direction)
When running a quick simulation with an assumed transformer impedance (using 10MVA rating) I come up with a reverse current flow through the transformer of 400A for faults on the utility side of the transformer supplied from the plant generator (ignoring plant motor contribution). Looking at this, it appears that the feeder breaker and main breaker 50/51 elements would not pickup for this fault flow however I'm not sure if the 51V element would detect this fault? Would the voltage collapse at the utility be enough to pickup the 51V for faults on the utility side of the transformer?
Also I'm still waiting to confirm the utility transformer winding configuration but if its a Delta-Wye configuration then the plant feeder or generator backup protection will not be able to see ground faults that occur on the Utility Delta side of the transformer. In this case would a 67N definitely be needed to detect these faults? If the transformer is a wye-Wye configuration then can the generator 50/51N and 501G as well as the plants feeder 50/51N see these external faults?
Maybe I'm incorrect here in assuming that the generator needs to trip for faults occurring on the utility side of the transformer but if it does not, then I see issues occurring when the utility re-closer tries to reclose and the generator is still online.
I appreciate any thoughts.