Detector Coverage for Clean Agent System 1

Status
Not open for further replies.

sv879

Mechanical
Dec 7, 2018
68
Dear Experts,

Most of the manufactures literature shows that photoelectric detectors installed for maximum area coverage of 250 ft² (23.2 m²) per detector.

Any idea where does the 250 ft² (23.2 m²) come from?
 
Replies continue below

Recommended for you

A typical analog or digital listed smoke detector intended to be connected to a FACP is designed for 30 Ft x 30 Ft spacing. The area of protection may be reduced based on air flow velocity. This is answer is based on NFPA 72 (2016 ed.)

 
sv879

Is the spacing due to requiring two detectors to activate, before the system dumps?


And if normal spacing, may delay activation?
 
I don't think so. I am talking about reduced spacing without cross zone/counting zone.

How come?

 