rockman7892
Electrical
- Apr 7, 2008
- 1,161
I am investigating the failure of a 2500kVA 13.2kV-480V transformer which appeared to have failed with internal winding failure. There was no failure analysis performed but there were visible burn marks on the windings and smoke was reported at the time of failure.
I was asked to perform PQ monitoring on the secondary of the transformer (480 Switchgear)in order to determine if several VFD's which are located downstream of the transformer could be causing harmonic issues which led to the transformer failure. The maximum current THD that was measured was 16% with the maximum Voltage THD being about 3.09%.
It is my understanding that the Harmonic Current Limits given in IEEE 519 are for application of the PCC with utility and are relatively meaningless when looking at harmonics downstream within an industrial facility. Are there any guidelines which dictate the maximum acceptable harmonic current distortion at a bus within an industrial system? My understanding has been that the harmonic current value is not really a problem by itself unless it is causing voltage distortion at the location. In this case the voltage distortion is only 3% so there does not appear to be an issue here?
Although there doesn't appear to be any significant harmonic distortion on the Bus, there is the possibility that the harmonic current is causing additional heating on the transformer. The maximum loading on the 2500kVA transformer during the monitoring period was about 1000kVA. Is it possible that 16% harmonic current could have caused additional heating on the transformer which caused its failure when only being loaded at 40%? Is there a "rule of thumb" for determining how much additional heating capacity harmonic current adds to the loading of a transformer in order to determine maximum transformer loading. I know IEEE Standard C57.110 " (IEEE Recommended Practice for Establishing Liquid-Filled and Dry-Type Power and Distribution Transformer Capability When Supplying Non-sinusoidal Load Currents")provides calculations for determining transformer capacity with harmonics but was wondering if there were any general guidelines or rules of thumb without having to carry out the calculations in this standard?
I was asked to perform PQ monitoring on the secondary of the transformer (480 Switchgear)in order to determine if several VFD's which are located downstream of the transformer could be causing harmonic issues which led to the transformer failure. The maximum current THD that was measured was 16% with the maximum Voltage THD being about 3.09%.
It is my understanding that the Harmonic Current Limits given in IEEE 519 are for application of the PCC with utility and are relatively meaningless when looking at harmonics downstream within an industrial facility. Are there any guidelines which dictate the maximum acceptable harmonic current distortion at a bus within an industrial system? My understanding has been that the harmonic current value is not really a problem by itself unless it is causing voltage distortion at the location. In this case the voltage distortion is only 3% so there does not appear to be an issue here?
Although there doesn't appear to be any significant harmonic distortion on the Bus, there is the possibility that the harmonic current is causing additional heating on the transformer. The maximum loading on the 2500kVA transformer during the monitoring period was about 1000kVA. Is it possible that 16% harmonic current could have caused additional heating on the transformer which caused its failure when only being loaded at 40%? Is there a "rule of thumb" for determining how much additional heating capacity harmonic current adds to the loading of a transformer in order to determine maximum transformer loading. I know IEEE Standard C57.110 " (IEEE Recommended Practice for Establishing Liquid-Filled and Dry-Type Power and Distribution Transformer Capability When Supplying Non-sinusoidal Load Currents")provides calculations for determining transformer capacity with harmonics but was wondering if there were any general guidelines or rules of thumb without having to carry out the calculations in this standard?