NFPA 13 11.2.3.2.3.3 “Where quick response sprinklers are used on a sloped ceiling or roof, the maximum ceiling or roof height shall be used for determining the percent reduction in design area.”
Its a light hazard occupancy building and has sloped ceilings, the maximum ceiling height is 19’-0”. NFPA 13 requires 1434 sq.ft. of system area of operation, including 30% for the sloped ceiling. The building also has a skylight (50 sq.ft approx.) , the maximum height on the skylight is 25’-0” above the finished floor. If this height is considered, the system area of operation requirement increases to 1950 sq.ft. One sprinkler head will provide coverage for the skylight.
So my question or confusion is- do I have to take into consideration the skylight height when calculating the design area reduction for quick response sprinklers? As the area of skylight is very small compared to rest of the room, I am not sure if this should dictate the system area of operation.
An interpretation on this code section would be appreciated.
Thank you !
Its a light hazard occupancy building and has sloped ceilings, the maximum ceiling height is 19’-0”. NFPA 13 requires 1434 sq.ft. of system area of operation, including 30% for the sloped ceiling. The building also has a skylight (50 sq.ft approx.) , the maximum height on the skylight is 25’-0” above the finished floor. If this height is considered, the system area of operation requirement increases to 1950 sq.ft. One sprinkler head will provide coverage for the skylight.
So my question or confusion is- do I have to take into consideration the skylight height when calculating the design area reduction for quick response sprinklers? As the area of skylight is very small compared to rest of the room, I am not sure if this should dictate the system area of operation.
An interpretation on this code section would be appreciated.
Thank you !