dl5150
Structural
- Sep 18, 2012
- 5
We are constructing pilecaps at site now which measures 1.6m x 5m x 1.3m deep and are each supported by 2 bored piles 800mm diameter. The piles are anchored 70mm from the base of the pilecap. The reinforcement of the piles are 12 pcs 25mm diameter epoxy coated bars and with 12mm spirals 80mm pitch. I have calculated the required development length in tension of 25mm to be 1.6 m. From the top of the pile, the 25 mm reinforcement can only extend at a maximum of 1.15m (juat a little below the 2nd layer top reinforcment of the pilecap. This is obviously not enough base on 1.6m which I have calculated.
In ACI 12.5 there is a 0.8 development length reduction factor for a 90 deg bend bar if stirrups are spaced not > 3db perpendicular to the bar being develop. I know this does not apply to our problem because the bars are straight vertically.
Is there any provision in ACI which states of a reduction in development length of straights bars in tension by enclosing them with ties? Thanks in advance
In ACI 12.5 there is a 0.8 development length reduction factor for a 90 deg bend bar if stirrups are spaced not > 3db perpendicular to the bar being develop. I know this does not apply to our problem because the bars are straight vertically.
Is there any provision in ACI which states of a reduction in development length of straights bars in tension by enclosing them with ties? Thanks in advance