This question relates mostly to footing and foundations. Specifically, development the pedestal bars (or dowels) that hook into the Footing or Foundation Slab.
I'm looking at a footing design in the PCA notes. In this example they require the full development length for bars in compression. They even imply that the designer needs to increase the thickness of the footing if this development length isn't met. This seems somewhat overkill based on my past experience.
The rationale given in the PCA notes is ACI code section 12.5.5 which says, "Hooks shall not be considered effective in developing bars in compression.""
What's not said in this example is WHY you need to develop these bars in compression. What type of failure are we going to see in these hooked bars if they are not developed in compression? For compression, I would personally be more worried about concrete bearing failure, soil failure or punching shear.
Is anyone out there actually using this compression development length as a requirement? I know that I've never worried about it much.
Walking through the logic, perhaps the issue is really that if you run all the numbers then section 12.2.5 and its reduction ""based on excess reinforcment"" reduces the development length of these bars to levels that don't realistically control. That sounds like a more reasonable path forward than the one given in the PCA notes.
What do you guys (and gals!) think? Is my take on this reasonable?
I'm looking at a footing design in the PCA notes. In this example they require the full development length for bars in compression. They even imply that the designer needs to increase the thickness of the footing if this development length isn't met. This seems somewhat overkill based on my past experience.
The rationale given in the PCA notes is ACI code section 12.5.5 which says, "Hooks shall not be considered effective in developing bars in compression.""
What's not said in this example is WHY you need to develop these bars in compression. What type of failure are we going to see in these hooked bars if they are not developed in compression? For compression, I would personally be more worried about concrete bearing failure, soil failure or punching shear.
Is anyone out there actually using this compression development length as a requirement? I know that I've never worried about it much.
Walking through the logic, perhaps the issue is really that if you run all the numbers then section 12.2.5 and its reduction ""based on excess reinforcment"" reduces the development length of these bars to levels that don't realistically control. That sounds like a more reasonable path forward than the one given in the PCA notes.
What do you guys (and gals!) think? Is my take on this reasonable?