SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
NFPA #20, 2013.
Been ages since I've done a diesel engine driven pump so please bear with me.
I have a 1,250 gpm diesel engine driven pump taking suction from a city water main with a flow test of 70 static, 40 residual flowing 1,500 gpm.
ESFR system and I need everything I can get.
Pump looks like it will be rated at 90, 95 or 100 psi and I will make that determination when I see the pump curves as I don't want churn to exceed 175 psi.
Let's assume we have a 95 psi pump with churn at 103 psi. 103 psi+70 psi=173 psi but:
4.18.1.2 Where a diesel engine fire pump is installed and where a total of 121 percent of the net rated shutoff (churn) pressure plus the maximum static suction pressure, adjusted for elevation, exceeds the pressure for which the system components are rated, a pressure relief valve shall be installed.
(103 psi*1.21=124.7 psi)+70 psi=194.7psi
I am 99% sure that in this case a pressure relief valve would be required, do you agree?
4.18.1.1* Pressure relief valves shall be used only where specifically permitted by this standard.
If I chose a 70 psi pump with a churn of 75 psi a relief valve would be prohibited by the standard.
(75 psi*1.21=90.75 psi)+70 psi=160.8 psi
Come to think of it in 45 years I don't think I've ever installed a diesel taking suction from the city... it's always been diesel engine driven vertical turbine pumps taking suction from a pond of which there's been at least half a dozen.
Been ages since I've done a diesel engine driven pump so please bear with me.
I have a 1,250 gpm diesel engine driven pump taking suction from a city water main with a flow test of 70 static, 40 residual flowing 1,500 gpm.
ESFR system and I need everything I can get.
Pump looks like it will be rated at 90, 95 or 100 psi and I will make that determination when I see the pump curves as I don't want churn to exceed 175 psi.
Let's assume we have a 95 psi pump with churn at 103 psi. 103 psi+70 psi=173 psi but:
4.18.1.2 Where a diesel engine fire pump is installed and where a total of 121 percent of the net rated shutoff (churn) pressure plus the maximum static suction pressure, adjusted for elevation, exceeds the pressure for which the system components are rated, a pressure relief valve shall be installed.
(103 psi*1.21=124.7 psi)+70 psi=194.7psi
I am 99% sure that in this case a pressure relief valve would be required, do you agree?
4.18.1.1* Pressure relief valves shall be used only where specifically permitted by this standard.
If I chose a 70 psi pump with a churn of 75 psi a relief valve would be prohibited by the standard.
(75 psi*1.21=90.75 psi)+70 psi=160.8 psi
Come to think of it in 45 years I don't think I've ever installed a diesel taking suction from the city... it's always been diesel engine driven vertical turbine pumps taking suction from a pond of which there's been at least half a dozen.