Dear FW Experts,
According to NFPA 20 section A.4.18.1, the fire water system has to be evaluated during when the diesel fire pumps are on overspeed scenario. The overspeed switch is typically set to limit at 10% of rated speed. A PSV is required if the piping component ratings are exceeded by the increase pressure generated from the overspeed. All this is true for the system I am currently looking at which is a diesel fire water pump (engine is water cooled supplied from the discharge)
Also the section mentions that since this case is relatively rare event, we are permitted to have the PSV discharge piped back to the suction side of the pump provided that we install another circulation relief valve (downstream of the main PSV) discharging to drain (or atmosphere) (section 4.18.7.1).
I would like to ask if somebody has any experience with this configuration. NFPA has clearly stated that it is an option but has not provided any basis on how to proceed with this design. What is the purpose of the additional circulation relief valve when the engine has its own cooling mechanism? How to determine the set point in relation ot the main PSV?
Thanks in advance for any input you provide.
Danger
According to NFPA 20 section A.4.18.1, the fire water system has to be evaluated during when the diesel fire pumps are on overspeed scenario. The overspeed switch is typically set to limit at 10% of rated speed. A PSV is required if the piping component ratings are exceeded by the increase pressure generated from the overspeed. All this is true for the system I am currently looking at which is a diesel fire water pump (engine is water cooled supplied from the discharge)
Also the section mentions that since this case is relatively rare event, we are permitted to have the PSV discharge piped back to the suction side of the pump provided that we install another circulation relief valve (downstream of the main PSV) discharging to drain (or atmosphere) (section 4.18.7.1).
I would like to ask if somebody has any experience with this configuration. NFPA has clearly stated that it is an option but has not provided any basis on how to proceed with this design. What is the purpose of the additional circulation relief valve when the engine has its own cooling mechanism? How to determine the set point in relation ot the main PSV?
Thanks in advance for any input you provide.
Danger