Can some one advise me on the following?
I recently witness a testing for a 300kVA Genset
I realize that typically the suppliers will be refering to their machine as 240kW at 0.8 power factor.
The test was done on a pure resisitive load
The manufacturers tried to pass the testing at 240kW loading and claiming it to be 100% loaded. Ie 240kW at P.F of 1
I insisted on a 300kW P.F 1 load test but was shot down by the others.
I need advice on the matter as I am unfamiliar with genset. Does a genset some how give constant kW independent of the P.F?
I recently witness a testing for a 300kVA Genset
I realize that typically the suppliers will be refering to their machine as 240kW at 0.8 power factor.
The test was done on a pure resisitive load
The manufacturers tried to pass the testing at 240kW loading and claiming it to be 100% loaded. Ie 240kW at P.F of 1
I insisted on a 300kW P.F 1 load test but was shot down by the others.
I need advice on the matter as I am unfamiliar with genset. Does a genset some how give constant kW independent of the P.F?