sebestie
Petroleum
- Jul 15, 2012
- 2
Hi
I am Commissioning Engineer on a Gas Plant Project. A piloted PRV is installed at the discharge of a firewater diesel pump. We tested the PRV (equipped with a pilot) on a certified test bench with air so that the opening pressure was set to 13.7 barg as specified in the PRV's datasheet.
When we installed the PRV and did a online test with the diesel firewater running increasing engine RPM but the PRV had still not opened at 15 barg.
The PRV's opening during inline test with firewater pump running was witnessed through an inline side-glass connected to the discharge flange of the PRV.
We decided to set the pilot in line with the pump running so that the PRV would open at 13.7 barg.
Then we dismantled the PRV to bring it back to the bench to test it again with air. The PRV opened at 12.1 barg instead of 13.7 barg.
The PRV discharge line goes back to the top of the Firewater tank, but The PRV is piloted so we can rule out any back pressure effect on the opening set pressure.
I am trying to find an explanation as why there is a difference in the opening pressure between the bench and inline?
Thanks
Seb
I am Commissioning Engineer on a Gas Plant Project. A piloted PRV is installed at the discharge of a firewater diesel pump. We tested the PRV (equipped with a pilot) on a certified test bench with air so that the opening pressure was set to 13.7 barg as specified in the PRV's datasheet.
When we installed the PRV and did a online test with the diesel firewater running increasing engine RPM but the PRV had still not opened at 15 barg.
The PRV's opening during inline test with firewater pump running was witnessed through an inline side-glass connected to the discharge flange of the PRV.
We decided to set the pilot in line with the pump running so that the PRV would open at 13.7 barg.
Then we dismantled the PRV to bring it back to the bench to test it again with air. The PRV opened at 12.1 barg instead of 13.7 barg.
The PRV discharge line goes back to the top of the Firewater tank, but The PRV is piloted so we can rule out any back pressure effect on the opening set pressure.
I am trying to find an explanation as why there is a difference in the opening pressure between the bench and inline?
Thanks
Seb