I am dealing with a nuisance tripping problem on a differential protection scheme and am looking for some help in understanding as this is a bit over my head. (We do have an engineer working on the problem as well)
The situation is we have a line up of GE 15KV switchgear with A and B side feeds and an automatic throw over system which among other things feeds 6 substation transformers (12.47KV to 480/277). A and B systems are redundant with each side having one 3000KVA, one 2500KVA and one 1500KVA transformer. Each breaker has differential protection with the primary CT’s located around the load side bus of each 12KV breaker and the secondary CT’s located around the bus stabs of the breakers in the 480V gear after the transformers. Each 12KV breaker has a T60 relay providing the protection. We ran interconnecting CT wiring from the secondary CT’s to the T60 relays. The problem is the 2 breakers feeding the 1500KVA transformers keep tripping on current, percent differential when only about 175A (@480V) of load is applied. One of the 2500KVA transformers is having the same issue.
What we discovered through some investigation is that the three breakers that are not nuisance tripping have CT ratio’s configured as follows:
2 3000KVA transformers have primary CT’s at 300:1 and secondary CT’s at 4000:1
1 2500KVA transformer has primary CT’s at 300:1 and secondary CT’s at 3200:1
The breakers that are tripping are configured as follows:
2 1500KVA transformers have primary CT’s at 100:1 and secondary CT’s at 2000:1
1 2500KVA transformer has primary CT’s at 100:1 and secondary CT’s at 3200:1.
It looks as though changing the 100:1 CT’s to 300:1 may fix our problem. Does this make any sense??
Thanks in advance for any input.
The situation is we have a line up of GE 15KV switchgear with A and B side feeds and an automatic throw over system which among other things feeds 6 substation transformers (12.47KV to 480/277). A and B systems are redundant with each side having one 3000KVA, one 2500KVA and one 1500KVA transformer. Each breaker has differential protection with the primary CT’s located around the load side bus of each 12KV breaker and the secondary CT’s located around the bus stabs of the breakers in the 480V gear after the transformers. Each 12KV breaker has a T60 relay providing the protection. We ran interconnecting CT wiring from the secondary CT’s to the T60 relays. The problem is the 2 breakers feeding the 1500KVA transformers keep tripping on current, percent differential when only about 175A (@480V) of load is applied. One of the 2500KVA transformers is having the same issue.
What we discovered through some investigation is that the three breakers that are not nuisance tripping have CT ratio’s configured as follows:
2 3000KVA transformers have primary CT’s at 300:1 and secondary CT’s at 4000:1
1 2500KVA transformer has primary CT’s at 300:1 and secondary CT’s at 3200:1
The breakers that are tripping are configured as follows:
2 1500KVA transformers have primary CT’s at 100:1 and secondary CT’s at 2000:1
1 2500KVA transformer has primary CT’s at 100:1 and secondary CT’s at 3200:1.
It looks as though changing the 100:1 CT’s to 300:1 may fix our problem. Does this make any sense??
Thanks in advance for any input.