We have had a number of spurious operations of line differential protection at 33kV on through-faults. The general situation is as follows. This has happened at a number of different points in the system.
System voltage: 33kV
Protection: HO2, HO4 "Translay" schemes. Setting minimum (0.4A), on 500/1 or 1000/1 CTs (and yes, I know it could be considered a bit low). Backup / #2 protection is IDMT overcurrent and earthfault. The CTs are a higher class than minimum suggested by relay manufacturer.
Pilot wire: Overhead "hardex", mixture of 4 and 5 core. Hardex is a steel earth wire laid around an internal pilot wire. The cores are not twisted, they are laid straight with PVC insulation. In appearance it is like a very heavily steel wire armoured PVC cable. The earth wire is not brought into the substation at the ends, but is earthed at each pole, because the fault current rating of the wire is below the fault levels.
Primary system: Two feeders from the source substation to the load substation, each with Translay protection. Feeder length typically 5-10km, loads 500-700A maximum per feeder. The feeders have lengths of 1-2km running in parallel, usually either side of the road (say 20m separation). Fault levels typically 6-10kA.
Scenario: Fault on one of the feeders results in (correct) trip at both ends by the diff protection. Second feeder trips at source end.
Anybody got any ideas? I don't even have any suggestions intelligent enough to use to "seed" any discussion!
Bung
Life is non-linear...
System voltage: 33kV
Protection: HO2, HO4 "Translay" schemes. Setting minimum (0.4A), on 500/1 or 1000/1 CTs (and yes, I know it could be considered a bit low). Backup / #2 protection is IDMT overcurrent and earthfault. The CTs are a higher class than minimum suggested by relay manufacturer.
Pilot wire: Overhead "hardex", mixture of 4 and 5 core. Hardex is a steel earth wire laid around an internal pilot wire. The cores are not twisted, they are laid straight with PVC insulation. In appearance it is like a very heavily steel wire armoured PVC cable. The earth wire is not brought into the substation at the ends, but is earthed at each pole, because the fault current rating of the wire is below the fault levels.
Primary system: Two feeders from the source substation to the load substation, each with Translay protection. Feeder length typically 5-10km, loads 500-700A maximum per feeder. The feeders have lengths of 1-2km running in parallel, usually either side of the road (say 20m separation). Fault levels typically 6-10kA.
Scenario: Fault on one of the feeders results in (correct) trip at both ends by the diff protection. Second feeder trips at source end.
Anybody got any ideas? I don't even have any suggestions intelligent enough to use to "seed" any discussion!
Bung
Life is non-linear...