Does the Differential Relay operate with zero current from on side and no internal fault?
Three single phase Generator/Transformer differential relays with percentage and harmonic restraint. They are GE model 12BDD15B relays. Tap setting is 2.9 Amp, zero restraint pickup 0.87 amps, 25% slope setting. Current transformers 4000/5 wye on the 13.8 kV sides and 400/5 delta on the 230 kV side of the transformer.
The full load current of the generator/transformer is 4.3 amps on the secondary side. The Gnerator is 13.8 kV, three phase wye grounded, and connected to a stepup transformer delta/ wye, 13.8 kV/230 kV. The question is: Do you disable the differential relays when you open the generator beaker but still the 230 kV and 13.8 kV are energized to feed the station service (load 300 kVA or 0.015 amps on the secondary) from the stepup transformer? The generator curerent transformers in this case are supplying zero current but the unbalance is far below the pickup current of the relays. Appreciate your input on the subject.
Three single phase Generator/Transformer differential relays with percentage and harmonic restraint. They are GE model 12BDD15B relays. Tap setting is 2.9 Amp, zero restraint pickup 0.87 amps, 25% slope setting. Current transformers 4000/5 wye on the 13.8 kV sides and 400/5 delta on the 230 kV side of the transformer.
The full load current of the generator/transformer is 4.3 amps on the secondary side. The Gnerator is 13.8 kV, three phase wye grounded, and connected to a stepup transformer delta/ wye, 13.8 kV/230 kV. The question is: Do you disable the differential relays when you open the generator beaker but still the 230 kV and 13.8 kV are energized to feed the station service (load 300 kVA or 0.015 amps on the secondary) from the stepup transformer? The generator curerent transformers in this case are supplying zero current but the unbalance is far below the pickup current of the relays. Appreciate your input on the subject.