I read in another forum or thread that you need to make sure that generators are the same pitch in order to operate them in parallel. This is done to prevent circulating currents.
If I connect only one three phase neutral wire on the running set is parallel to handle the single phase loads how will I get circulating currents?
I used a properly sized contactor to switch between the generators in case one shut down and I made sure the single phase loads did not exceed the value of the rated generator.
I used this system to parallel 2 Cummins Engines and 1 Cat rental set for a hospital job.
I had no circulating currents.
Did I do something wrong? I mean it worked and the Cat was a different pitch from the 2 Cummins engines. The Cat was a 1 Meg set and the Cummins sets were 1 Meg each. I commissioned the system while working for a parallel controls manufacture.
Please let me know if my thinking is incorrect but don’t you need a common tied neutral to have circulating currents?
Thanks
If I connect only one three phase neutral wire on the running set is parallel to handle the single phase loads how will I get circulating currents?
I used a properly sized contactor to switch between the generators in case one shut down and I made sure the single phase loads did not exceed the value of the rated generator.
I used this system to parallel 2 Cummins Engines and 1 Cat rental set for a hospital job.
I had no circulating currents.
Did I do something wrong? I mean it worked and the Cat was a different pitch from the 2 Cummins engines. The Cat was a 1 Meg set and the Cummins sets were 1 Meg each. I commissioned the system while working for a parallel controls manufacture.
Please let me know if my thinking is incorrect but don’t you need a common tied neutral to have circulating currents?
Thanks