WWTEng
Structural
- Nov 2, 2011
- 391
Consider a 3'x12' deep pier foundation supporting an out door structural column. The contact tor was supposed to pour a pipe within the concrete. The contractor forgot to do that. They are recommending digging down to one side of the pile 9' deep to install the pipe and fill the void with grout.
I am not a huge fan of this approach. I think once the native soil is removed, the skin friction will be difficult to replicate with the grout. I also don't understand the "dig to one side" of the pile. I think it would be impossible to not cave in the soil on other sides.
I think I should have them remove and replace with a bigger pile.
Any thoughts?
Thank you.
I am not a huge fan of this approach. I think once the native soil is removed, the skin friction will be difficult to replicate with the grout. I also don't understand the "dig to one side" of the pile. I think it would be impossible to not cave in the soil on other sides.
I think I should have them remove and replace with a bigger pile.
Any thoughts?
Thank you.