We have proven the regulator to be fuctioning correctly by running the DVR in a running plant.
The auxiliary circuits (from the PLC) to the DVR are functioning correctly.
The problem seems to be between the DVR and the generator:
Voltage Sensing Circuit - 3 Phase?
PMG circuit - 3 phase?
Field - DC?
Whilst synchronised we have no excitation control. I understand we could be operating the generator in the wrong quadrant?
What are the affects of reversing the Sensing Voltages? PMG circuit? the field? and is this the issue - sensing / excitation is 120 degrees out of phase?
When the generator is not synchronised (No Load) to the utility we can fully regulate the voltage +/- 10% by varying excitation - as expected.
Should we excite the generator at 411Volts or below and then synchronise the utility pulls us down to 385V causing excessive VARs.
Or should we excite the generator to 412Volts or above and synchronise the utility pulls us up to 440V causing the sytem to trip on over voltage.
If you can help it would be much appreciated.
Cheers
PS When synchronised (and working correctly) the DVR initially excites in kVAr mode until the Real Generator Current is within 15% output current, then PF control takes priority - this is not the case as can been seen above, as we are trapped high or low.
The auxiliary circuits (from the PLC) to the DVR are functioning correctly.
The problem seems to be between the DVR and the generator:
Voltage Sensing Circuit - 3 Phase?
PMG circuit - 3 phase?
Field - DC?
Whilst synchronised we have no excitation control. I understand we could be operating the generator in the wrong quadrant?
What are the affects of reversing the Sensing Voltages? PMG circuit? the field? and is this the issue - sensing / excitation is 120 degrees out of phase?
When the generator is not synchronised (No Load) to the utility we can fully regulate the voltage +/- 10% by varying excitation - as expected.
Should we excite the generator at 411Volts or below and then synchronise the utility pulls us down to 385V causing excessive VARs.
Or should we excite the generator to 412Volts or above and synchronise the utility pulls us up to 440V causing the sytem to trip on over voltage.
If you can help it would be much appreciated.
Cheers
PS When synchronised (and working correctly) the DVR initially excites in kVAr mode until the Real Generator Current is within 15% output current, then PF control takes priority - this is not the case as can been seen above, as we are trapped high or low.