Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Dimensionnal of cable ? 1

Status
Not open for further replies.

etienned

Industrial
Feb 17, 2004
2
How can we define the right main cable compare with the power supply ( 1900W - 2200W, etc..).To be sure a solution is to take main cable of 1.5mm2 diameter, but if we want to decrease this section, how can we estimate the right section, the number of wire, etc...

Thanks
 
Replies continue below

Recommended for you

Your cable CSA is determined by current, not power. So either tell us the current directly, or tell us the voltage you are supplying the load from. Also let us know the type of load, because if it is a motor or similar inductive load, the power factor will have to be taken in to account when determining the current.






-----------------------------------

Start each new day with a smile.

Get it over with.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor