This is a 13.8KV:480 2000KVA pad mounted transformer with a primary fuse protected by pole mounted 65 amp fuses.
I usually feed to a panel board or a LV switch gear (depending on ratings) from the secondary of the transformer. I would like to feed two 1200 amp MCC. Therefore I would normally feed the MCC from a breaker in the switch gear. However the customer engineer does not want the switch gear. If either MCC goes down, the process goes down so his point is that if he ever wants to service the MCC mains, he will open the primary switch. The MCC's would have main breakers and each MCC would have a separate set of cables from the transformer secondary to feed the MCC. Both MCC would be located in the same room. He says that the primary fuse will protect the cables on short circuit and the MCC main breaker will protect the cables from overload. The MCC rating would be 65KA the short current on the secondary is 40KA or less.
I think this shouldn’t be done unless the there is a single MCC to avoid two services into the building and the cables and terminations on the MCC breaker should be rated for the full secondary current that likely would flow until the primary fuse blows which would be about 3700 amps. But I’d prefer to limit the MCC bus to 1200 amps to limit the available energy. I don’t want to make the customer spend money on switchgear he doesn’t need and I need to give him a strong case if I’m going to insist. Am I being too conservative? What say you? Are there parts of the code I can point too?
I usually feed to a panel board or a LV switch gear (depending on ratings) from the secondary of the transformer. I would like to feed two 1200 amp MCC. Therefore I would normally feed the MCC from a breaker in the switch gear. However the customer engineer does not want the switch gear. If either MCC goes down, the process goes down so his point is that if he ever wants to service the MCC mains, he will open the primary switch. The MCC's would have main breakers and each MCC would have a separate set of cables from the transformer secondary to feed the MCC. Both MCC would be located in the same room. He says that the primary fuse will protect the cables on short circuit and the MCC main breaker will protect the cables from overload. The MCC rating would be 65KA the short current on the secondary is 40KA or less.
I think this shouldn’t be done unless the there is a single MCC to avoid two services into the building and the cables and terminations on the MCC breaker should be rated for the full secondary current that likely would flow until the primary fuse blows which would be about 3700 amps. But I’d prefer to limit the MCC bus to 1200 amps to limit the available energy. I don’t want to make the customer spend money on switchgear he doesn’t need and I need to give him a strong case if I’m going to insist. Am I being too conservative? What say you? Are there parts of the code I can point too?