Directional earth fault relay maloperation

Status
Not open for further replies.

RRaghunath

Electrical
Aug 19, 2002
1,732
Directional earthfault relay receives VT input from the VT in the switchgear incomer cable box and CT input from that in the transformer neutral-to-earth connection. The relay is set to look away from the transformer.

Now, can some one tell me - whether the VT location is the reference for the directionality or the CT location? I think it is the CT location.
 
Replies continue below

Recommended for you

The phase angle difference between the zero-sequence voltage measured by the VTs and the zero-sequence current measured by the CT is what determines the direction. So, it takes both, with proper polarity, to have directionality.
 