Good morning everyone.
I'm looking for help in understanding a recent incident that happened locally. During regular maintenance, a couple of technicians were performing testing on a 13.8kV/230kV D-Y generator step up transformer. One of their tests was winding resistance measurements using a Multi-Amp 830280 transformer ohmmeter. During their testing, they were running into issues with getting the readings to stabilize on the high side windings, so it was decided that they would go against the instructions in the manual for test lead set-up. The manual states that only one end of the winding under test is to be grounded, and all others are to be left ungrounded. Our standard practice for the high side is to leave H0 grounded, and to short and ground the low side windings with copper braid. I know from experience that when moving from one winding to the next (ie H2 to H3), it can sometimes take between 5 to 10 minutes for the resistance to "break" and start to fall to expected levels. The technicians performing the test were not seeing any drop after 2 minutes, so the decision was made to short and ground all windings that were not under test. I believe they were working on H2, so H1 and H3 were shorted to H0 (which was left grounded), X1-3 remained shorted and grounded. They performed the test again and were able to get the results they were expecting.
The test set was discharged and Technician 1 removed the current and potential leads from H2. Technician 2 was to remove the braid from H3 to move it to H2. As the 230kV bushings are quite tall, a fiberglass ladder modified to be rested against the bushings was used to access the top. Technician 2 was halfway down the ladder with the braid in one hand when a flash and discharge occurred. Technician 1 heard the "crack", Technician 2 described the flash as having someone flash a camera in his face. Technician 2 felt a slight shock through his arm.
No one is quite sure exactly why this happened. I'm curious if anyone would have any input into this occurrence. Some of the details are as follows: Test set was being operated at 5A (which is the correct, and maximum, output of this particular ohmmeter). Weather conditions were damp/misty. Test leads had been disconnected at least 10 seconds prior to the discharge. Fiberglass ladder was described as "in good condition". There was no apparent second point of contact. This was an older test instrument that had been replaced with a Tettex winding resistance instrument that operates at 50A, however it had been sent out for repairs. The multi-amp transformer ohmmeter was last calibrated in 2003.
My instant thought was that the test set had been left on, and Technician 2 was in contact with the winding just as Technician 1 lifted the leads, causing a dv/dt voltage spike, but we were assured the test set was "discharged" and the leads were removed quite some time before the discharge occurred. I'm not sure if the test set was turned off or unplugged, which is our standard practice prior to moving leads. I'm trying to understand the impact of grounding multiple windings while performing the testing, contrary to the instruction manual.
Does anyone have any thoughts as to why this happened?
Thank you for your input.
I'm looking for help in understanding a recent incident that happened locally. During regular maintenance, a couple of technicians were performing testing on a 13.8kV/230kV D-Y generator step up transformer. One of their tests was winding resistance measurements using a Multi-Amp 830280 transformer ohmmeter. During their testing, they were running into issues with getting the readings to stabilize on the high side windings, so it was decided that they would go against the instructions in the manual for test lead set-up. The manual states that only one end of the winding under test is to be grounded, and all others are to be left ungrounded. Our standard practice for the high side is to leave H0 grounded, and to short and ground the low side windings with copper braid. I know from experience that when moving from one winding to the next (ie H2 to H3), it can sometimes take between 5 to 10 minutes for the resistance to "break" and start to fall to expected levels. The technicians performing the test were not seeing any drop after 2 minutes, so the decision was made to short and ground all windings that were not under test. I believe they were working on H2, so H1 and H3 were shorted to H0 (which was left grounded), X1-3 remained shorted and grounded. They performed the test again and were able to get the results they were expecting.
The test set was discharged and Technician 1 removed the current and potential leads from H2. Technician 2 was to remove the braid from H3 to move it to H2. As the 230kV bushings are quite tall, a fiberglass ladder modified to be rested against the bushings was used to access the top. Technician 2 was halfway down the ladder with the braid in one hand when a flash and discharge occurred. Technician 1 heard the "crack", Technician 2 described the flash as having someone flash a camera in his face. Technician 2 felt a slight shock through his arm.
No one is quite sure exactly why this happened. I'm curious if anyone would have any input into this occurrence. Some of the details are as follows: Test set was being operated at 5A (which is the correct, and maximum, output of this particular ohmmeter). Weather conditions were damp/misty. Test leads had been disconnected at least 10 seconds prior to the discharge. Fiberglass ladder was described as "in good condition". There was no apparent second point of contact. This was an older test instrument that had been replaced with a Tettex winding resistance instrument that operates at 50A, however it had been sent out for repairs. The multi-amp transformer ohmmeter was last calibrated in 2003.
My instant thought was that the test set had been left on, and Technician 2 was in contact with the winding just as Technician 1 lifted the leads, causing a dv/dt voltage spike, but we were assured the test set was "discharged" and the leads were removed quite some time before the discharge occurred. I'm not sure if the test set was turned off or unplugged, which is our standard practice prior to moving leads. I'm trying to understand the impact of grounding multiple windings while performing the testing, contrary to the instruction manual.
Does anyone have any thoughts as to why this happened?
Thank you for your input.