Discharge Piping from Non-integral Separately Fired Superheater

Status
Not open for further replies.

Old Cowhand

Mechanical
May 31, 2017
2
0
0
US
I am reviewing some design blueprints for a plant expansion that has not yet been commissioned. Part of the design includes a non-integral superheater fed from a branch steam line. The piping to the superheater is marked non-boiler code, but the piping out of the superheater is marked boiler code until the first valve. I was under the impression that piping to and from a non-integral superheater was all non-boiler code. Why would the superheater outlet piping be considered boiler code? The engineering firm that did the design is no longer in business or I would ask them. Thanks in advance.
 
Replies continue below

Recommended for you

Thanks Jeff. Sorry I wasn't clear; I was referring to boiler code. I believe my situation is shown on 100.1.2(B3) which shows a non-integral superheater. This drawing is also included as 58.3.1C in older ASME Section I codes. This drawing shows steam piping to and from the superheater as non-boiler external piping, falling under Pressure piping. But the engineering firm has the superheater outlet steam piping as boiler external piping, falling under Boiler and Pressure Vessel Code. Any thoughts?
 