AusLee
Electrical
- Sep 22, 2004
- 259
Hello,
I'm talking about a normal 12,000 BTU air condition fed from one single phase circuit breaker in a panel board several rooms away.
The NEC (?) state that there shall be a nearby (line of sight And less than 15m) disconnect switch for this kind of deivces.
The Australian / NewZealand code state that this 2 pole disconnect switch can be removed if the breaker feeding the appliance can be secured in the Off position.
I follow all codes at the same time and i have 2 questions:
1. The breaker is a normal miniature 32A, can you please point out one type pf those that can be secured in position? The only ones i know are moulded case type.
2. The HVAC guy tells me Thank you for paying for this to protect me but i don't need it. I ask why and he has a point: he says that the split AC is made of 2 units, one indoor and one outdoor, and i'm installing this near the indoor one so he says when he goes outside to service the radiator, someone might trip this 2 pole disconnect switch inside the room and he will still get electrocuted. So either i install yet a second one for him outside, or forget this idea.
I agree with him and feel that this article is for "window" units. The project is a hospital and we have a whole bunch of those so the savings from taking them out is not negligible.
I would like to ask what do you think? Can a "letter" from the HVAC guy be shown if the "Inspector" comes and asks why doesn't these units have a DP switch (by the way does it Have to be two-pole or just disconnecting the phase is enough, same for 3~, shall it be 3P or 4P for a Y system? I know i can call the Inspector and ask but i want ot know Internationally how ths goes. Thank you.
I'm talking about a normal 12,000 BTU air condition fed from one single phase circuit breaker in a panel board several rooms away.
The NEC (?) state that there shall be a nearby (line of sight And less than 15m) disconnect switch for this kind of deivces.
The Australian / NewZealand code state that this 2 pole disconnect switch can be removed if the breaker feeding the appliance can be secured in the Off position.
I follow all codes at the same time and i have 2 questions:
1. The breaker is a normal miniature 32A, can you please point out one type pf those that can be secured in position? The only ones i know are moulded case type.
2. The HVAC guy tells me Thank you for paying for this to protect me but i don't need it. I ask why and he has a point: he says that the split AC is made of 2 units, one indoor and one outdoor, and i'm installing this near the indoor one so he says when he goes outside to service the radiator, someone might trip this 2 pole disconnect switch inside the room and he will still get electrocuted. So either i install yet a second one for him outside, or forget this idea.
I agree with him and feel that this article is for "window" units. The project is a hospital and we have a whole bunch of those so the savings from taking them out is not negligible.
I would like to ask what do you think? Can a "letter" from the HVAC guy be shown if the "Inspector" comes and asks why doesn't these units have a DP switch (by the way does it Have to be two-pole or just disconnecting the phase is enough, same for 3~, shall it be 3P or 4P for a Y system? I know i can call the Inspector and ask but i want ot know Internationally how ths goes. Thank you.