I have a query regarding an installation where there is an upstream 400A MCCB supplying several 1ph 32A type D MCBs.
According to the manual of the 400A MCCB, the ground fault current setting is set at 80A with 0.2s tripping time.
However, at 80A, the 32A MCB downstream only trip as overload at ~2s, so discrimination fails.
Is the design ground fault current or the tripping time wrong that should be adjusted to achieve discrimination?
Thanks
PK