Mohamed Mowafy
As we know, if we want to adopt the direct analysis method in steel design, there are some steps to fulfill the code requirement.
1: reducing stiffness by 0.8
2: Assign the slenderness factors K major and K minor for all members by 1.00.
3: applying the notional load as a percentage of gravity load, say 0.003 w in each floor, to be included with all gravity load combinations, and in some cases it must be included in lateral load combinations.
4: Perform P-delta analysis for all design cases and combinations.
In fact, applying notional load in some software is complicated, so I tried to figure out its effect on members design ratio, and my conclusion is that if your case is designing low-rise buildings such as warehouses, notional load doesn't have a tangible effect on design ratio.
In the case of residential multi-story buildings less than 6 floors and heavy industrial buildings, the effect is around 2-3% increase in design ratio.
In my opinion, considering notional loads in low-rise buildings is time-wasting, but it's effective in high-rise buildings.
So, in my opinion, considering stiffness reduction in the direct analysis method is enough to get a fair result.
I need to see your opinion on this subject, and thanks