I have a building with a plan area of 140ft x 58ft. This gives an overall aspect ration of 2.4, not a problem. However, when looking at the section of this building the roof is divided (see attached). There is a clear story in the center. If i look at the aspect ratio for each half I get a ratio of 4.8, problem.
I do not know if i can count on this complete 58ft roof to act as a single acceptable diaphragm, or do i need to count for it as two separate ones? The short vertical clear story will be sheathed in wood it does have many openings but i can utilize decent panels between windows for shear transfer as required.
I am wondering what your opinions are on the acceptable vs run-away nature of this building and what are some serious concerns you may have with the lateral loading in the 140ft length.
As per AWC 2008 Table 4.2.4
Max Diaphragm Aspect Ratios for Slope Diaphragms
Blocked Wood Structural panels = 4:1
Unblocked Wood Structural panels = 3:1
Roof System
I-joist rafters, no ceiling joists
Low eave=9ft, Top of 5' clear story=22ft, highest eave=30ft
The center wall will be full height 2x6 studs and i probably will be sheathing it in wood for the in-plane loading.
I will be checking deflection... just haven't yet
I do not know if i can count on this complete 58ft roof to act as a single acceptable diaphragm, or do i need to count for it as two separate ones? The short vertical clear story will be sheathed in wood it does have many openings but i can utilize decent panels between windows for shear transfer as required.
I am wondering what your opinions are on the acceptable vs run-away nature of this building and what are some serious concerns you may have with the lateral loading in the 140ft length.
As per AWC 2008 Table 4.2.4
Max Diaphragm Aspect Ratios for Slope Diaphragms
Blocked Wood Structural panels = 4:1
Unblocked Wood Structural panels = 3:1
Roof System
I-joist rafters, no ceiling joists
Low eave=9ft, Top of 5' clear story=22ft, highest eave=30ft
The center wall will be full height 2x6 studs and i probably will be sheathing it in wood for the in-plane loading.
I will be checking deflection... just haven't yet