loribadeaux
Chemical
- Sep 13, 2006
- 4
I need some advice for the following proposed scenario:
HP fuel gas of 40-55bar is sent to a conditioning skid consisting of coalescer, heater and pressure reduction station.
There is a concern that in case of rupture/ puncture in the system (equipment or piping) the resulting released gas will ignite and the resulting flame can damage the piperack in the vicinity.
The first way against this kind of scenario would be fire protection measures for the piperack. The client do not want to do this.
So we've done a dispersion modelling and jet flame length calculation and the conclusion was that a max. 10m flame is acceptable; this flame length was to be achieve if the pressure is max.20bar and the flow rate about 5000kg/h of fuel gas.
In conclusion a flow orifice was proposed to be installed upstream the skid which will limit the flow rate to max. 5000Kg/h. But obvious the pressure loss through the orifice will not be enough to lower the pressure from 40-55 to 20bar so I believe that the proposed FO will not help too much with our possible safety problem.
I would like to hear some opinions regarding the proposed solution with the FO.
Thank you very much.
Lori
HP fuel gas of 40-55bar is sent to a conditioning skid consisting of coalescer, heater and pressure reduction station.
There is a concern that in case of rupture/ puncture in the system (equipment or piping) the resulting released gas will ignite and the resulting flame can damage the piperack in the vicinity.
The first way against this kind of scenario would be fire protection measures for the piperack. The client do not want to do this.
So we've done a dispersion modelling and jet flame length calculation and the conclusion was that a max. 10m flame is acceptable; this flame length was to be achieve if the pressure is max.20bar and the flow rate about 5000kg/h of fuel gas.
In conclusion a flow orifice was proposed to be installed upstream the skid which will limit the flow rate to max. 5000Kg/h. But obvious the pressure loss through the orifice will not be enough to lower the pressure from 40-55 to 20bar so I believe that the proposed FO will not help too much with our possible safety problem.
I would like to hear some opinions regarding the proposed solution with the FO.
Thank you very much.
Lori