TheRichYS
Mechanical
- Nov 3, 2006
- 3
Can anybody help me on calculation of getting dissipating heat from transformer? I guess there is a chart or something that I can get the heat that comes out from transformer.
I need the quantity of heat dissipated from 3 transformers in kcal or in Joule
I need this information to calculate the size of the Exhaust fan and supplying louver for substation room.
Room Size: 85'-4"(L) x 30'(W) x 18'(H)
Location: side of the building
Sizes of 3 transformers in substation room:
TR1
2000KVA, 13857.5V, 45.31A, 1066KW, PF=1
TR2
2667KVA, 13840V, 58.13A, 1296KW, PF=-0.96
TR3
2667KVA, 13872.5V, 27.81A, 634KW, PF=1
Supplying Air Temperature via Supplying Louver = 70F
Current Room Temperature of Substation Room = 90F
Thank you very much for your kind replies in advance.