Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Distillery Ethanol process and Storage Tanks

Status
Not open for further replies.

Bill3752

Chemical
Jan 24, 2008
133
0
0
US
I have come across some distilleries that are applying NFPA as follows to atmospheric tanks (designed to 1 oz/in2:
1. Have automatic sprinkler systems - F factor = .3.
2. There is verbiage in NFPA that states that for ethanol can take another 50% reduction on top of that - i.e. F factor = .15.

Anyone have experience with this? Must tanks be designed to a specific standard to incorporate this?

Off hand, taking this level of credit scares me.

 
Replies continue below

Recommended for you

Doesn't NFPA require the fire protection to be a Fixed Waterspray System meeting NFPA 15?

A sprinkler system meeting NFPA 13 with normally closed sprinkler heads isn't equivalent to a waterspray system with open nozzles.
 
Status
Not open for further replies.
Back
Top