I work more in generation, not distribution, but if I remember correctly, here in Oregon a Tier 1 net metering interconnect application is pretty much rubber stamped approved if it's a maximum of 25 kVA, connected via an approved inverter, and the total DG on the feeder is less than 10% of the maximum connected load on the feeder (15% if it's solar PV), etc. Might be missing a couple of small items there, but I think the last part of my sentence is key. If it would exceed the percentage of load limit, I think trying to add new DG to the feeder triggers an engineering study as part of the Tier 2 interconnect application. I bet no homeowner will want to pay that added cost and will bail on the idea, therefore the unbalance on the single-phase feeder phases is likely limited by both requirements, probably to an amount that can be handled by nearby voltage regulators.