Hello, I was perusing the MA structural docs as shown in the attached image:
Screenshot_20230303-140931_r2rton.png


I'm trying to get my head wrapped around how to interpret uniform distributed vs point load. I understand distributed can be used to calculate total weight capacity of a room, and point load explains why I, a 200 lb person, can stand within a 1 sqft area. My confusion is to what extent (area) can I apply a point load? I suppose this level of detail starts to get into the actual structural design of the room ... Any help is much appreciated!

*Edit: in the above, I used the term point load interchangeably with concentrated
 
Replies continue below

Recommended for you

Concentrated loads are typically applied uniformly over a 2.5 foot by 2.5 foot area unless otherwise specified (such as for vehicle barriers, etc.).
 
When looking at decking or sheathing, 2.5ftx2.5ft as OldDawg mentioned is normal. I know a few engieners who prefer to do 1ftx1ft. When looking at a joist or beam or stringer, a point load is a point load.
 
That 2.5'x2.5' is spelled out somewhere, it's not just assumption on the part of the user (it's in 4.4 in ASCE 7-16, for example).
The grating manufacturers have their own definition.
Edit: I see a separate definition for stair treads in 4.16.
 
Ah now I see it in the standard:

[tt]"Unless otherwise
specified, the indicated concentration shall be
assumed to be uniformly distributed on a floor or
roof over an area of 2.5 feet square [6.25 ft (0.58 2
m )] and shall be located so as to produce the 2
maximum load effects in the structural members."[/tt]

This kinda also answers another question I had regarding where exactly is the point load. If I'm reading the quote correctly, it would be in the worst possible location e.g. maybe in the center of a room away from a load-bearing wall.
 
That’s a large area for a point load. Real point loads are often much pointier than that.
 