We are having a bit of a debate in my local group of utilities regarding where lightning arrestors should be placed wrt disconnect switches on radial disitrbution systems.
We all agree that the lead lengths (both 'hot' and 'ground') need to be kept to a minimum wrt the equipment being protected, but we are not in agreement when it comes to the disconnects.
One group favours putting the arrestor on the 'line' side of the switches that isolate cable dips, transformers, reclosers, etc so that they are still 'in-service' when the device is isolated.
The other group feels that although the chance of lightning damaging a transformer/cable/etc is remote if its cutout switch is open, you would still be removing the only lightning protection available to the xmfr if the arrestor were to be placed on the line side. In addition, it is easier to keep the lead lengths shorter when the arrrestor is on the load side of the switch.
Is there a definitive standard or study done to resolve this? Assume that we are not willing to pay for arrestors on BOTH sides.
We all agree that the lead lengths (both 'hot' and 'ground') need to be kept to a minimum wrt the equipment being protected, but we are not in agreement when it comes to the disconnects.
One group favours putting the arrestor on the 'line' side of the switches that isolate cable dips, transformers, reclosers, etc so that they are still 'in-service' when the device is isolated.
The other group feels that although the chance of lightning damaging a transformer/cable/etc is remote if its cutout switch is open, you would still be removing the only lightning protection available to the xmfr if the arrestor were to be placed on the line side. In addition, it is easier to keep the lead lengths shorter when the arrrestor is on the load side of the switch.
Is there a definitive standard or study done to resolve this? Assume that we are not willing to pay for arrestors on BOTH sides.