Distribution transformer 2000KV Ou

Status
Not open for further replies.

engrajapon

Electrical
May 10, 2017
1
Distribution transformer 2000KVA,11000V/433V

Primary current=104.97A
Secondary current=2666.82A

So the CT ratio for the load side energy meter will be 3000/1A

but i need to calculate from the below cause
Output load around 1600KW/If the load 1200KW what will be the energy meter CT ratio selection
 
Replies continue below

Recommended for you

Same, you need to size the CT on maximum load so that it can accommodate the distribution transformer loading.
 