Do pumps need to be separated from each other by a wall? 1

Status
Not open for further replies.

jejaram

Electrical
Feb 9, 2011
45
0
0
CO
Hi

Recently I was visiting a power station and someone mentioned there were new requirements by NFPA 20 for pumps to be physically separated from each other by a wall. I've never seen this anywhere. I read through NFPA 20 and did not find anything regarding this matter.

Could someone please confirm or most likely deny this assertion?
 
Replies continue below

Recommended for you

Section 4.14 has a lot about protection but I can't see anything about pumps needing to be separate. Think it might be a misunderstanding about separation of a fire pump room or building?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Pump room needs a fire barrier from the rest of the building but pumps themselves do not need a separation between other pumps.
 
NFPA 20-2022 4.21.2.1 goes so far as to say that multiple pumps are required to be installed in the same room, when installed in a series arrangement, unless permitted otherwise by 4.21.2.2.
 