Paragraph 401.2 of the 2012 IMC requires mechanical ventilation for dwelling units if the infiltration is less than 5 AC/hr (0.667 cfm/sf with an 8-foot ceiling) at a differential pressure of 0.2 iwg.
Paragraph C402.4.1.2.3 of the 2012 IECC doesn't allow the leakage to exceed 0.4 cfm/sf (3 AC/hr with an 8-foot ceiling) at a differential pressure of 0.3 iwg.
Converting the limit using the formula Q = c * (delta_P)^n , and with n = 0.65:
The IMC limit translates to 6.5 AC/hr at delta_P = 0.3 iwg.
So in a blower door test at 0.3 iwg:
1) IECC doesn't allow leakage to exceed 3 AC/hr
2) IMC doesn't allow natural ventilation unless the infiltration exceeds 6.5 AH/hr.
Are these conflicting limits code-speak for, "Don't use natural ventilation in dwelling units?"
If so, why didn't they just say that in Paragraph 401.2 of the 2012 IMC?