gemotorres
Civil/Environmental
- Feb 25, 2014
- 5
I have a question for underground precast structures, specifically rectangular or square boxes, vaults, if I need to check Shear for the floor slab design. I have seen that in several references like Precaster Notebook, a design from Delta Engineering for a CSX Cooper-E80 load and other colleagues, and I checked it always getting thicker slabs, but I found another design example where the Shear was not checked in the floor only in for punching in the top slab.
In other blog here referred to checking shear in concrete slabs somebody commented that : "there is an statement in the Bridge Code saying Shear is not needed to be checked when the slab is designed as a two-way slab" , or did he mean for Top slabs only??
Is this the reference mentioned there?:
"18.4.9 Shear Check of Slab
Slab bridges designed for dead load and (HL-93) live load moments in conformance with LRFD
[4.6.2.3] may be considered satisfactory in shear LRFD [5.12.2.1]." from WisDOT Bridge Manual.
I would appreciate your advice and comments. Thanks.
In other blog here referred to checking shear in concrete slabs somebody commented that : "there is an statement in the Bridge Code saying Shear is not needed to be checked when the slab is designed as a two-way slab" , or did he mean for Top slabs only??
Is this the reference mentioned there?:
"18.4.9 Shear Check of Slab
Slab bridges designed for dead load and (HL-93) live load moments in conformance with LRFD
[4.6.2.3] may be considered satisfactory in shear LRFD [5.12.2.1]." from WisDOT Bridge Manual.
I would appreciate your advice and comments. Thanks.