Maybe it seems bizzare for some of you.
I have this situation:
A three-phase squirrel-cage 4 poles motor drives a centrifugal pump.
Motor has following parameters: 90kW nominal power, 160A nominal current, 0.86 power factor at nominal power and 0.95 efficiency at nominal power, class S1, 1500rpm.
Pump has following parameters: rated power 73kW, maximum power 90.1kW, efficiency 0.74, rated capacity 295 mc/h, total developed head 80m, speed 1485 rpm.
We started to use the pump and we expected to make the required capacity. But instead of this at aprox.157 Amps measured we receive only 80% of capacity at the pump (236 mc/h instead of 295 mc/h). In process we need the nominal capacity. But we cannot open the discharge valve more because we try to avoid motor tripping. The motor is installed in a hazardous area so we set the overload protection at nominal current as the standards says.
The designers tells us the most cheaper way to reach the nominal capacity is by installing a VFD to reduce the motor speed and release the discharge valve more.
I made some calculations and it seems it doesn't works because the torque will be higher because it flows more product in pump. The only benefit of installing a VFD is more efficiency, which means at same capacity the motor need less power, but what happens when we reduce the motor speed and increase the rotor torque (pump capacity)?
What do you think? Can a VFD solve the problem and WHY?
Thank you all!!
I have this situation:
A three-phase squirrel-cage 4 poles motor drives a centrifugal pump.
Motor has following parameters: 90kW nominal power, 160A nominal current, 0.86 power factor at nominal power and 0.95 efficiency at nominal power, class S1, 1500rpm.
Pump has following parameters: rated power 73kW, maximum power 90.1kW, efficiency 0.74, rated capacity 295 mc/h, total developed head 80m, speed 1485 rpm.
We started to use the pump and we expected to make the required capacity. But instead of this at aprox.157 Amps measured we receive only 80% of capacity at the pump (236 mc/h instead of 295 mc/h). In process we need the nominal capacity. But we cannot open the discharge valve more because we try to avoid motor tripping. The motor is installed in a hazardous area so we set the overload protection at nominal current as the standards says.
The designers tells us the most cheaper way to reach the nominal capacity is by installing a VFD to reduce the motor speed and release the discharge valve more.
I made some calculations and it seems it doesn't works because the torque will be higher because it flows more product in pump. The only benefit of installing a VFD is more efficiency, which means at same capacity the motor need less power, but what happens when we reduce the motor speed and increase the rotor torque (pump capacity)?
What do you think? Can a VFD solve the problem and WHY?