Does combinations of actions need for ultimate limit state verification as well? or it's just for the serviceability limit state verification?

for the Serviceability limit state (SLS) check

E.g: for a domestic building, snow and seismic. Combination would be as follows
Design load = [total permanent] + [ψ1.00 x leading variable] + [ψ0.7 x trailing variable]


for the Ultimate limit state (ULS) check
Design load = 1.35Gk (permanent) + 1.5Qk (variable)

Is the above correct or does the combinations (snow, seismic) should be checked for ultimate limit state (ULS) as well?.

Screenshot_2022-11-30_at_8.44.00_pm_xualw1.png
 
Replies continue below

Recommended for you

Look at equations 6.9 and 6.10 in clause 6.4.3.2

and A1.3 where you got that table from!
 

The title of thread is ' Does combinations of actions need for ultimate limit state verification as well? Eurocode 2 '

A= yes .. if you are looking for ULS ( strength, stability , ...)

Q= for the Ultimate limit state (ULS) check
Design load = 1.35Gk (permanent) + 1.5Qk (variable)

Is the above correct or does the combinations (snow, seismic) should be checked for ultimate limit state (ULS) as well?.

A= You are expected to consider other combinations for ULS including ( wind , seismic, ..)

I will suggest you to look to the following doc. and try to ask more specific questions..