BigJohn1
Electrical
- May 24, 2003
- 57
I had to ground the low-side wye on a 5MVA 13,200Δ:480Y transformer, afterwards we began tripping out on inrush when trying to energize with no secondary load.
Nothing else about the installation changed except bonding the 480V wye to ground.
I don't know what inrush was when the wye was floating, but once grounded we recorded slightly over 300A on the high side, which was tripping the 300A instantaneous protection.
We enabled a cold-load pickup feature that temporarily increases instantaneous to 2X for 30 cycles after closing, and this allowed us to stay online.
Why would a ground reference on a transformer cause this?
Nothing else about the installation changed except bonding the 480V wye to ground.
I don't know what inrush was when the wye was floating, but once grounded we recorded slightly over 300A on the high side, which was tripping the 300A instantaneous protection.
We enabled a cold-load pickup feature that temporarily increases instantaneous to 2X for 30 cycles after closing, and this allowed us to stay online.
Why would a ground reference on a transformer cause this?