A 200 Amp overhead service feeds an outdoor 200A fused disconnect on the outside of the house. Circa about 1960.
3 - #3/0 wires in metal conduit go from that disconnect, through the crawlspace 50', to a 200 Amp panel board in the middle of the house.
The conduit is bonded with a short piece of copper tubing at the disconnect switch outside. I'm saying this is the main bonding jumper.
But there is no ground rod at that location, instead the conduit was bonded where it entered the panelboard to a line that went directly to the underground water pipe on the neutral.
A few years ago the panel inside was changed to a 200A circuit breaker panelboard instead of the fused panel. The electrician installed a short piece of PVC conduit between the floor and the crawlspace to get the #3/0 installed to the new panel board. The rest of the 50' run of metal conduit remained untouched. As with the other panel that was taken out, all the neutrals and equipment grounds are on the neutral bar. I'm thinking that the metal pipe was the ground electrode conductor, it got chopped off - but its still grounded via the neutral that's tied to the ground at the panelboard.
MY QUESTION.... do these grounds need to be separated with separate ground bars to the branch circuits? Can I put a jumper around the PVC ... but what real good does that do ? as it's grounded via the neutral at the disconnect.
3 - #3/0 wires in metal conduit go from that disconnect, through the crawlspace 50', to a 200 Amp panel board in the middle of the house.
The conduit is bonded with a short piece of copper tubing at the disconnect switch outside. I'm saying this is the main bonding jumper.
But there is no ground rod at that location, instead the conduit was bonded where it entered the panelboard to a line that went directly to the underground water pipe on the neutral.
A few years ago the panel inside was changed to a 200A circuit breaker panelboard instead of the fused panel. The electrician installed a short piece of PVC conduit between the floor and the crawlspace to get the #3/0 installed to the new panel board. The rest of the 50' run of metal conduit remained untouched. As with the other panel that was taken out, all the neutrals and equipment grounds are on the neutral bar. I'm thinking that the metal pipe was the ground electrode conductor, it got chopped off - but its still grounded via the neutral that's tied to the ground at the panelboard.
MY QUESTION.... do these grounds need to be separated with separate ground bars to the branch circuits? Can I put a jumper around the PVC ... but what real good does that do ? as it's grounded via the neutral at the disconnect.