As mentioned above, the primary conductor centering's affect on accuracy is a function of the CT design (secondary winding design) and also the magnitude of the magnetic field. For most normal metering applications, if the primary conductor is off slightly, then the affect on accuracy is typically negligable. For generator applications, where the primary current is very high >6,000A, then local core saturation can be caused by mis-aligned primaries. Local core saturation is also a function of the secondary winding design, in that for generation CTs, most secondaries are made from segmented windings.
To answer your question in short, there is not too much general data available for the primary conductor affect on accuracy, mainly because it depends on so many factors. If you really want to be sure, then you have to test the actual CT under simulated conditions, which is normally not too hard to do.